Viewing 3 replies - 1 through 3 (of 3 total)
  • Author
    Replies
  • #108357

    Tony Athens
    Moderator
    Vessel Name: Local Banks
    Engines: QSB 6.7 550 HP
    Location: Oxnard, CA
    Country: USA

    You now know nor than I do on this.. Go for it..

    #108326

    Gene Fuller
    Participant
    Vessel Name: Yorkshire Rose
    Engines: QSB5.9 380
    Location: Punta Gorda, Florida
    Country: USA

    The VDO documents mention yellow and red as the thermocouple wire colors. Also, the range of the gauge is up to 1650 F.

    Both of these would indicate Type K.

    The extension wire is not too critical as long as all the connections are kept at the same temperature. The accuracy will be degraded a bit, but that may not be too important in this application. Trends are probably more important than absolute numbers.

    Disclaimer: I have worked a lot with thermocouples in an industrial laboratory setting, but not as a mechanic or engine specialist.

    #108316

    Tony Athens
    Moderator
    Vessel Name: Local Banks
    Engines: QSB 6.7 550 HP
    Location: Oxnard, CA
    Country: USA

    Thermocouple type–Saving a few bucks

    The only answer to your ?? will come come a complete spec for the type of thermocouple the VDO gage uses.. A quick peek at the spec sheet did not show the specs.

    A easy Google Search yielded this Cut & Paste:

    The primary differences between the two thermocouples: K & J Types ( most common)

    Measuring Range…
    Type K = -330Ā°F to +2460Ā°F (-200Ā°C to +1250Ā°C)
    Type J = -40Ā°F to +1382Ā°F (-40Ā°C to +750Ā°C)

    Sensitivity…
    Type K = approximately 41 ĀµV/Ā°C
    Type J = approximately 55 ĀµV/Ā°C

Viewing 3 replies - 1 through 3 (of 3 total)